aadamson said:
Ok, so here is my basic problem with one breaker...
Now you are saying it takes 10 amps of current to trip the breaker, and yet that's 3 more amps than either the 7 amp or the 5 amp seperates would take( I made those numbers up, as I don't know actually what each individual value is, but each alone is less than the 10A).
I'm kinda new here, so pardon me for the following somewhat tangential monologue. It doesn't really answer the one vs. two breaker question. But I think that has already essentially been answered. One breaker is fine, or two breakers are fine. Whichever you choose. But here's some basic info on how to size your breakers.
When sizing a "standard" rated breaker, the 80 percent rule applies for continuous load circuits. In other words, you shouldn't load the breaker with more than 80 percent of the expected continuous current. So for a 10 amp breaker, you should never connect more than 8 amps of "continuous" load. (Continuous is defined in the National Electric Code, or NEC, as "a load where the maximum current is expected to continue for three hours or more.")
It's important to remember that the breakers are there to protect the wiring and the power source, not the load. Most radios (i.e. expensive loads) have some sort of internal Over Current Protection Device (OCPD) such as a fuse or thermal cutoff switch. I haven't looked inside of an SL30 so I don't know what internal protection it has, if any. But as far as the aircraft wiring circuit breaker is concerned, the radio is expendable.
With a radio system, the maximum load is usually generated when transmitting. So using the 3-hour defintion, you should never see a "continuous load" from your SL30. Therefore you could look in the specs for the "nominal" operational load for your sizing.
There's a lot of science and math behind the sizing of breakers. You can study the breaker's characteristic trip curve, which takes into account time and thermal factors, in addition to overall load.... And then, some breakers are "100% rated" rather than standard rated, which means they can take 100 percent of the continuous load rather than the 80 percent... Which really means that they were tested at higher loads or under different thermal conditions than the standard breakers....
You can see that its easy to get wrapped around the axle on this topic. So I just keep it simple and use the 80 percent rule.
Happy wiring!