My name is also Joe and I agree with the other Joe. We Joes stick together.

The purpose of the 60 amp ANL fuse is to protect the wiring from excessive battery current in case the alternator shorts out. If the alternator "B" lead is connected to the main buss, then the 60 amp fuse should be located at the main buss. Engine starting current should NOT go through the 60 amp fuse.
Why are you using a 60 amp circuit breaker? A 60 amp ANL fuse is capable of carrying the full alternator output without nuisance blowing.
An alternator is self current limiting. It is not physically capable of putting out much more than than its rated capacity. If enough loads are added to the alternator output, the voltage will drop, thus preventing an increase in current much beyond the alternator capacity. Under those conditions, the alternator could overheat if not adequately cooled.
Joe Gores