My old compressor has a motor data plate that says 240 volts and 15 amps, so I wired a dedicated circuit with 35 feet of #12 Romex and a 20 amp breaker. I've never had any problems with it. Today I upgraded to a compressor with a motor that says FLA 21.5. My understanding is that this means the motor draws 21.5 amps when making it's full rated power (5 HP). My question is whether I have to rewire with #10. I know that #12 is only used for up to 20 amps, and the new motor can draw 21.5, but I also know that 35 feet is pretty short and the motor probably draws far less than the full 21.5 amps. I've looked at the voltage drop calculations and I get 1.22 volts versus .76 volts. It hardly seems worth the time and money to change it out. I guess I'll also add that the wiring run is inside conduit on an exterior wall and that I will be moving in the near future and removing it anyway. I'd love to hear from some knowledgeable electrical folks. Thanks.
__________________
Steve Zicree
Fullerton, Ca. w/beautiful 2.5 year old son
RV-4 99% built and sold
Rag and tube project well under way

paid =VAF= dues through June 2013
Reply With Quote
  #2  
Old 07-18-2008, 07:01 PM
Mark Burns's Avatar
Mark Burns Mark Burns is offline
 
Join Date: Jan 2005
Location: Ruston, Louisiana
Posts: 878
Default You'll be fine

As long as you don't install a breaker larger than the 20 amp you will be safe.
You probably knew that.

So the answer is no, you don't have to rewire.
If your compressor was really loaded and started tripping the breaker, then you would need to rewire with #10 and a 30 amp breaker.

Mark


Quote:
Originally Posted by szicree View Post
My old compressor has a motor data plate that says 240 volts and 15 amps, so I wired a dedicated circuit with 35 feet of #12 Romex and a 20 amp breaker. I've never had any problems with it. Today I upgraded to a compressor with a motor that says FLA 21.5. My understanding is that this means the motor draws 21.5 amps when making it's full rated power (5 HP). My question is whether I have to rewire with #10. I know that #12 is only used for up to 20 amps, and the new motor can draw 21.5, but I also know that 35 feet is pretty short and the motor probably draws far less than the full 21.5 amps. I've looked at the voltage drop calculations and I get 1.22 volts versus .76 volts. It hardly seems worth the time and money to change it out. I guess I'll also add that the wiring run is inside conduit on an exterior wall and that I will be moving in the near future and removing it anyway. I'd love to hear from some knowledgeable electrical folks. Thanks.
__________________
Mark Burns
Ruston, Louisiana
RV-7A N781CM 1,650+ hrs
FFI FL-24
A&P

Last edited by Mark Burns : 07-18-2008 at 07:06 PM.
Reply With Quote
  #3  
Old 07-18-2008, 09:39 PM
cytoxin's Avatar
cytoxin cytoxin is offline
 
Join Date: Apr 2006
Location: south carolina
Posts: 1,111
Default

put an amp probe on it, see what it really pulls then go from there. it will likely be ok.
__________________
William Weesner/ still kicking.
Reply With Quote
  #4  
Old 07-19-2008, 08:34 AM
MrNomad's Avatar
MrNomad MrNomad is offline
 
Join Date: Mar 2006
Location: Tucson, AZ
Posts: 823
Default wire is cheap

Like plumbing, when you try to squeeze too many amps thru a wire too small or marginal, you create heat and waste electricity. 35 feet is not short.

If you want the motor to last longer and wish to conserve electricity, oversize is better than not. Wire is cheap, motors are not especially when you are in the middle of painting and the compressor dies.

Barry
Reply With Quote
  #5  
Old 07-19-2008, 10:08 AM
airguy's Avatar
airguy airguy is offline
 
Join Date: Oct 2006
Location: Garden City, Tx
Posts: 5,122
Default

The motor is rated at 21.5 Full Load Amps - but that assumes a full 5 horsepower output. The motor is going to be slightly larger than required for the full-pressure compressor load, it's likely the compressor will only be drawing 4 or 4.5 horsepower, not 5, which will decrease somewhat the electrical draw on the motor.

If you have an amprobe, use it to determine your actual full-load draw. Personally, I wouldn't change it out until/unless you start tripping the 20 amp breaker. DO NOT put a 30-amp breaker on the circuit unless you upgrade the wire. In my experience, you're probably going to be tripping it at 20 amps with a 5hp compressor, I set mine up from the start on a 30-amp breaker.
__________________
Greg Niehues - SEL, IFR, Repairman Cert.
Garden City, TX VAF 2020 dues paid
N16GN flying 700 hrs and counting; IO360, SDS, WWRV200, Dynon HDX, 430W
Built an off-plan RV9A with too much fuel and too much HP. Should drop dead any minute now.
Reply With Quote
  #6  
Old 07-19-2008, 10:20 AM
cytoxin's Avatar
cytoxin cytoxin is offline
 
Join Date: Apr 2006
Location: south carolina
Posts: 1,111
Default

the LRA is likely 3 times that of the running current.( locked rotor amperage ) you will see this on start up every time and the more pressure in the tank the higher it will be..)
you can set your cut in pressure lower to decrease this if it is at the threshold of being to much.
__________________
William Weesner/ still kicking.
Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -6. The time now is 12:36 AM.


The VAFForums come to you courtesy Delta Romeo, LLC. By viewing and participating in them you agree to build your plane using standardized methods and practices and to fly it safely and in accordance with the laws governing the country you are located in.