  #1  
Old 09-27-2012, 07:12 PM
LAMPSguy's Avatar
LAMPSguy LAMPSguy is offline
 
Join Date: Feb 2008
Location: Pensacola, FL
Posts: 374
Default Electrical question (Shop)

I am having a 240V outlet with a 60A breaker put in for my wife's pottery kiln. Contractor recommended a separate outlet and breaker (at an additional $100) for the compressor. I will never run them at the same time, so I figured I would save money and just plug in what I want to use, but he says the breaker is too high for the compressor????

I thought the breakers protect the wiring from excess current, not the device plugged in.

He says IF there was a problem with the compressor it would pull to much current before breaker tripped and screw up my comp motor?

Any contractors/EE's here to confirm or deny what I need?
__________________
RV-? in planning stages.
RV-14 #140050 SOLD

Permanently willing to contribute fuel for RV rides

Helicopter ATP/CFI(I)
ASEL/AMEL Commercial/Inst/CFI(I)
Aerobatic Instruction available

Atlanta based.
Reply With Quote
  #2  
Old 09-27-2012, 07:23 PM
ColoRv's Avatar
ColoRv ColoRv is offline
 
Join Date: Apr 2012
Location: Tampa (BKV)
Posts: 926
Default

I've done the exact same thing you are suggesting many times. This afternoon I did exactly that for my new house...welder/air compressor circuit.

Your toaster doesn't pull 15 amps...but it's on a 15 amp circuit. Your TV doesn't pull 15 amps either. Neither does your computer, or most anything else in your house, but they are on oversized breakers. Circuit breakers protect the house wiring, not the unit plugged in. Find another electrician....yours is trying to take you for a ride.

PS. I am a contractor, though it wouldn't take a tradesman to tell you the above.
__________________
RV-8 Flying
1,235th flying RV8
SARL Race#95
SnF Homebuilt Judge

2015 Sun n Fun Kit Built Reserve Grand Champion
2015 Oshkosh Kit Built Champion
2015 Jeffco Kit Built Grand Champion
2014 Oshkosh Outstanding Workmanship Award

Broken Warrior of the Jarhead Clan

Last edited by ColoRv : 09-27-2012 at 07:31 PM.
Reply With Quote
  #3  
Old 09-27-2012, 07:24 PM
David Z David Z is offline
 
Join Date: Aug 2010
Location: Thunder Bay Ontario
Posts: 335
Default

Plug it in and don't worry about it.
If your compressor motor sucks back that much power, the motor is already fried.
__________________
RV-8
Empennage Passed Pre-close Inspection
Wings mostly done
Fuselage is "in the mail"
83126
Dash 8 day job is financing the RV-8
Donation till September 2021
Reply With Quote
  #4  
Old 09-27-2012, 07:28 PM
catmandu's Avatar
catmandu catmandu is offline
 
Join Date: Dec 2005
Posts: 917
Default

Electrical panel breakers are to protect the wires from turning into magma and burning down your house with you and your loved ones in it. The electrical code could give a rodent's arse about protecting the devices you plug in.
__________________
Mike C.
Sierra Nevada
RV-6A bought flying
Reply With Quote
  #5  
Old 09-27-2012, 07:35 PM
LAMPSguy's Avatar
LAMPSguy LAMPSguy is offline
 
Join Date: Feb 2008
Location: Pensacola, FL
Posts: 374
Default Thanks

Yeah, thats what I thought...best to double check though.

Can't really get another company, and the price quoted was $50 less than what I paid in my last house for the same (but didnt have compressor). I am in base housing and in order to do this I have to use pre-selected contractor, bids, etc, etc military money ****...then I have to pay to have it removed when I leave!

BUT, a few hundred $ so my wife will stop squawking about the kiln...priceless!
__________________
RV-? in planning stages.
RV-14 #140050 SOLD

Permanently willing to contribute fuel for RV rides

Helicopter ATP/CFI(I)
ASEL/AMEL Commercial/Inst/CFI(I)
Aerobatic Instruction available

Atlanta based.
Reply With Quote
  #6  
Old 09-27-2012, 08:12 PM
ColoRv's Avatar
ColoRv ColoRv is offline
 
Join Date: Apr 2012
Location: Tampa (BKV)
Posts: 926
Default

Base housing. Understood. Just tell him you're not going to use the compressor after all. Adios.

Thanks for your service. Semper Fi.
__________________
RV-8 Flying
1,235th flying RV8
SARL Race#95
SnF Homebuilt Judge

2015 Sun n Fun Kit Built Reserve Grand Champion
2015 Oshkosh Kit Built Champion
2015 Jeffco Kit Built Grand Champion
2014 Oshkosh Outstanding Workmanship Award

Broken Warrior of the Jarhead Clan
Reply With Quote
  #7  
Old 09-27-2012, 10:34 PM
Coolerfixer Coolerfixer is offline
 
Join Date: Jan 2011
Location: Idaho
Posts: 10
Exclamation

Sorry, I have to agree with the electrician. I have my sparky license and would never knowingly do as you asked.
You need to to look at the data plate on your compressor/motor. It should have maximum fuse/breaker size listed on it. You can also calculate the correct circuit size using Ohm's Law if the rating is in watts (Watts/Volts=Amps). A common misconception is that the breaker is ONLY there to protect the conductors (wires) in the building. Would you plug your toaster into a 200 amp protected circuit? I sure wouldn't!
The point of all circuit protection is to prevent fires and personal injury,including death. If what you are plugging into that outlet is not rated for 60 amps, it can very easily cause a fire. 60 amps will make 10 gauge wire glow red hot long before it would trip a breaker. 10 gauge or smaller is what your cord is if your compressor is 7hp or smaller.
There is an overload in some compressor motors. I wouldn't bet my life or anybody else's on a 3 cent part from China. Your compressor motor may have an LRA (locked rotor amperage) rating listed. I have seen LRA's over 150 amps which would trip a 60 amp breaker obviously, but depending on what size motor you have, your LRA is probably less than 60.
The NEC most certainly does address appliance wiring external to the building wiring, anyone who says otherwise knows not of what they speak. If your compressor didn't come with a pre-installed cord, it was meant to be hard wired. The instructions that came with it may cover that.
Sorry if this comes across as a rambling rant, but I see this kind of DIY/handyman electrical far too often, and it can and will kill you.
__________________
Mike Deleve


RV-9 emp kit
2012 Donation paid
Reply With Quote
  #8  
Old 09-28-2012, 01:22 AM
ColoRv's Avatar
ColoRv ColoRv is offline
 
Join Date: Apr 2012
Location: Tampa (BKV)
Posts: 926
Default

I've never seen an air compressor without its own thermal protection. Regardless, the NEC allows for oversize on breakers to allow for startup draw unless something drastic has changed since last I had this discussion with one of our engineers, which I doubt.

Still, I was curious so I did a web search and found this discussion between electricians about breaker size for a 5hp air compressor install.

Quote:
"The breaker can be sized at up to 350% of the full load current to allow starting without tripping the breaker.
That means you can use a breaker as large as 98 amps (actually 100 would be allowed).
Quote:
The OP has the correct idea that the motor protects itself against overload with built in thermal protection and thus cannot overload the feed, and all the breaker is doing is protecting the feed conductors against short circuit damage.

125% of full load motor current for the wires, and up to 350% of the full load current for the breaker.

So yes, you can see breakers significantly larger than what is typical for general use branch circuits based solely on wire size.
I'll not lose any sleep over my compressor running on my welding circuit anymore than I would about my iPhone charging on a 15a circuit, but as in all things we each must live with our own decisions.
__________________
RV-8 Flying
1,235th flying RV8
SARL Race#95
SnF Homebuilt Judge

2015 Sun n Fun Kit Built Reserve Grand Champion
2015 Oshkosh Kit Built Champion
2015 Jeffco Kit Built Grand Champion
2014 Oshkosh Outstanding Workmanship Award

Broken Warrior of the Jarhead Clan

Last edited by ColoRv : 09-28-2012 at 01:27 AM.
Reply With Quote
  #9  
Old 09-28-2012, 04:40 AM
Captain_John's Avatar
Captain_John Captain_John is offline
 
Join Date: Jan 2005
Location: KPYM
Posts: 2,686
Default

Quote:
Originally Posted by LAMPSguy View Post
I thought the breakers protect the wiring from excess current, not the device plugged in.
True,

How do you plan on terminating the #6 60amp wires in the motor housing?

If you trim them down, you will have say... #12's fused at sixty amps.

Hmmmm... that doesn't sound good at all!

As an electrician, THAT is your violation. It used to be table 310.16 but they just changed it this past code to something like 310.15.b.16 or something like that. Same table with a few changes. I can cite the new one for you if you really need it.

Aside from that, yes, the motor has it's own thermal protection and if you can keep the wires FULL size to the motor, use the 60 ampere male configuration on the compressor and do everything else like supporting, disconnecting means and not violate any UL listings by modifying equipment (that's gonna be a tuffy here once you try to get those big wires to the compressor's pressure switch... see article 110.3b) you will be legal.

I would like to see how you plan on getting 60 amp wires in there, though...

Let me know what you come up with! I am glad to help out!

CJ
__________________
RV-7 Flying - 1,200 Hours in 5 Years!
The experiment works!
TMX-IO-360, G3i ignition & G3X with VP-X
Reply With Quote
  #10  
Old 09-28-2012, 07:32 AM
Wayne Gillispie Wayne Gillispie is offline
 
Join Date: Apr 2009
Location: USA
Posts: 1,499
Default

I have seen oversized breakers cause fires inside heat pumps, condensers and electric furnaces and yes all of them had thermal overloads.

Read the data plate or installation instructions on most any larger electrical appliance in your home. It will provide you with "Max fuse or breaker size".

Contrary to what many learn building their plane, it is not just to protect the feed wiring.

Talk to a fire marshall, most house fires don't start in the properly sized feed circuits, usually in the appliances.

Install a smoke detector near equipment.
__________________
Good judgment comes from experience, and a lot of that comes from bad judgment.
Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -6. The time now is 05:13 AM.


The VAFForums come to you courtesy Delta Romeo, LLC. By viewing and participating in them you agree to build your plane using standardized methods and practices and to fly it safely and in accordance with the laws governing the country you are located in.